Water heater weeping

So, I finally got tired of the water heater hi temp/hi pressure valve weeping/leaking down onto the electrical connections to the solenoids...and eventually down the side of the RV. The factory design by Suburban left a little to be desired. After replacing the valve, and still leaking, I verified the water temp wasn't too high, and my well cuts off at 60 pounds, so my incoming pressure wasn't too high.... and changing out the control board is a major PITA, given where the installers have placed it, so I just accepted that it would intermittently dribble.
So I made a way for it to dribble directly into the city water connection box, directly below the water heater and thus out the trap door, and onto the ground, bypassing all of the electrical connections....by adding a length of 3/4" PEX pipe, and drilling a 1" hole in the sheet metal floor of the water heater housing.
I didn't exactly address the cause, but I did address the results....I'm satisfied for now.

Regards
Gemstone
__________________

__________________
No longer on the road.
Gemstone is offline   Reply With Quote
Old 03-04-2013, 10:46 AM   #2
golf_bears
Senior Member
 
Join Date: May 2007
Location: West Bend, Wisconsin
Posts: 397
Sounds like a good solution. Perhaps you've lost the air gap/space in the tank? It bleeds out after a while and needs to be replaced periodically.
__________________

golf_bears is offline   Reply With Quote
Old 03-04-2013, 08:10 PM   #3
netjam
Senior Member
 
Join Date: May 2011
Location: Canadian on the Road
Posts: 101
Gemstone.....good solution. Tried the air into the top of tank thing (didn't work) and eventually drilled a hole in the water heater cover for a hose. Connected the prv with a hose going out the hole in the cover so the weeping would fall harmlessly to the ground.
__________________
2012 F-350
2011 Escalade 37RE
netjam is offline   Reply With Quote
Old 03-04-2013, 10:55 PM   #4
billr
Senior Member
 
Join Date: Jan 2006
Location: Ontario Canada
Posts: 857
The relief valve is not bad to replace. 10 min job. Picked one up at Ace hardware $15 no more weeping. There is a special tool to remove it available. Its like a strange shaped socket. Maybe can cut up a large deep socket and slide on it to turn it loose. I borrowed one from a friend. You have to remove the metal shroud to get it out.

The seat in the valve gets calcium build up and unseats when the pressure is dropped. Maybe can be cleaned and put back in. I just went with a new one.

Can't believe I let it leak so long off and on.

Bill
__________________
Bill and Joan
4 Collie pups
05 M/S 38RL3 #2046
01 Volvo VNL770
05 Smart Passion Loaded piggyback
https://picasaweb.google.com/billandjoan
Weigh-It Portable RV Scales
https://www.weighitrv.com
billr is offline   Reply With Quote
Old 03-05-2013, 08:22 AM   #5
2blackdogs
Senior Member
 
Join Date: Jan 2006
Posts: 105
Gemstone,
I had the same problem and it's easily remedied.
Turn off the main water supply and go inside and turn on the hot water faucet and let it drain until it stops. This puts a small amount of air in the tank.
The water heater needs an air pocket to allow for expansion of the hot water. If the air pocket is not there there is only one place for the water to go as it expands and that is out of the relief valve.
If you have already did this you may have purchased a defective replacement.????
Over the years I have sold hundreds and hundreds of relief valves, big and small, and a few have been defective but I think your main problem is the air pocket.
__________________
2006 Elite Suites 36TK3
2001 F-550 Starhauler
Kelderman Air ride
Trailer Saver hitch
www.mytripjournal.com/elitesuitestravels
IN GOD WE TRUST
2blackdogs is offline   Reply With Quote
Old 03-06-2013, 04:29 PM   #6
rjohnsonnm
Senior Member
 
Join Date: Sep 2005
Location: Albuquerque, NM
Posts: 112
Actually, air in the top of the water heater is not a good thing. The oxygen causes corrosion, leading to a new water heater sooner. When the hot water expands the pressure is automatically relieved by the hot water backing up into the supply line leading to the water heater, just like in your house. The only time you want an air cushion is to prevent water hammer (which is not your problem), and you don't put the air in the water heater. If you still have the problem, you probably have a defective valve from the store. One thing you might try is to open the valve when it's pressurized and let it snap shut. Be careful if the water is hot. I have to do that when I fill the system at the beginning of the season. It weeps for a few minutes and then stops. Running a drain from the relief valve is really not something that you should have to do. (BTW, I was a Machinist Mate in the Navy for 10 years, so I've worked with a lot of water systems)
Ron
__________________
Ron and Betty
2004 Mobile Suites 36RS3 #0925
2011 F-350 Lariat Diesel Longbed
Albuquerque, NM
rjohnsonnm is offline   Reply With Quote
Old 03-07-2013, 10:15 AM   #7
Motor31
Senior Member
 
Join Date: May 2005
Posts: 2,130
Actually, given the design of the RV water heaters, air in the tank is a good thing. There is a check or anti back flow valve on the inlet line to the water heater that prevents pressure from backing back into the water line, pressurizing it to beyond it's capacity and creating a leak. It also prevents the water heater from trying to heat the water in the line outside the heater so that it is not constantly running. That same check valve is the one that create a humming sound when it starts to go bad as you use the hot water. There is a similar valve on the shore water inlet connection point to prevent the water pump from dumping water out of the rig when you turn it on while dry camping. The RV system is quite different from the boiler in a naval ship.

The suburban manual I have for my rig on page 6 specifically states to prevent the dripping or weeping from the pressure relief valve you should allow an air pocket to be formed inside the tank. The instructions state; "This air pocket will form in the tank by design. However it may be diminished by use". They follow that statement with instructions for reforming the air pocket. by turning off the inlet water, opening a faucet inside then opening the pressure relief valve until water stops flowing out of it. At that point close the valve, faucet and open the water line in that order. Doing so will reduce or eliminate the weeping from the valve as the water expands due to heating. An additional option is to install an accumulator tank.
__________________
Mike Nancy and the fuzzies
Fulltiming since June 2004
Volvo 660 MH tow vehicle
2005 MS 38RL
2007 Saturn Ion "toad"
2010 Gold Wing "piggyback"
Motor31 is offline   Reply With Quote
Old 03-07-2013, 12:54 PM   #8
rjohnsonnm
Senior Member
 
Join Date: Sep 2005
Location: Albuquerque, NM
Posts: 112
I stand corrected. Obviously RV water heaters and home water heaters are not piped the same. Mea culpa.
Ron
__________________
Ron and Betty
2004 Mobile Suites 36RS3 #0925
2011 F-350 Lariat Diesel Longbed
Albuquerque, NM
rjohnsonnm is offline   Reply With Quote
Old 03-07-2013, 07:20 PM   #9
Gemstone
Senior Member
 
Join Date: Jun 2006
Location: Boydton, VA
Posts: 443
"Turn off the main water supply and go inside and turn on the hot water faucet and let it drain until it stops. This puts a small amount of air in the tank"....
Yep, done that. It does not weep all the time....just when it feels like it...no rhyme or reason.
So, with my overflow pipe extended, I don't care how ofter it gets a wild hair and decides to leak, 'cause now it goes out on the ground, not down the side of the rig.
Thanks for the comments...it's what sets this forum apart.

Regards
Gemstone
__________________
No longer on the road.
Gemstone is offline   Reply With Quote
Old 03-24-2013, 10:24 AM   #10
RodeWorthy
Senior Member
 
Join Date: Oct 2005
Location: Woodstock, Ontario
Posts: 370
Gemstone,
Good solution. I did much the same but the discharge is out the side. Yours is no doubt safer. One would not want to stand in front of my pipe when opening the valve. After replacing the valve I have had very little discharge.

Pictures show the tool Billr mentioned. It could easily be fabricated but I couldn't resist it when it was in my hand at RV Connections in Yuma.

I also installed an accumulator and that has been a great boon when working off the pump while dry camping.
Attached Images
File Type: jpg dscf7859r_194.jpg (47.7 KB, 106 views)
File Type: jpg relief_valve_removal_tool_189.jpg (44.3 KB, 106 views)
File Type: jpg dscf7866r_815.jpg (33.5 KB, 106 views)
File Type: jpg dscf7865r_192.jpg (44.6 KB, 106 views)
__________________
RodeWorthy

'07 Mobile Suites 36RS3 #3910
Mor/ryde IS, Trailersaver TS3 hitch
Level-Up with Remote Control
4 x 135W Solar Panels, Outback Controller, 4 x 6V batteries, Xantrex Inverter/Charger
'08 Chevy 3500 dually Duramax/Allison
RodeWorthy is offline   Reply With Quote
Old 03-25-2013, 08:57 AM   #11
Gemstone
Senior Member
 
Join Date: Jun 2006
Location: Boydton, VA
Posts: 443
Yep, that looks like a good solution too....anything to prevent water from dripping on the solenoid valve connections....I can't believe the stupid feat of engineering by Suburban...

Regards
Gemstone
__________________
No longer on the road.
Gemstone is offline   Reply With Quote
Old 03-25-2013, 01:32 PM   #12
Carny Bill
Senior Member
 
Join Date: Nov 2005
Location: Illinois-summer,winter-some where else
Posts: 336
Weeping

Only to be outdone by dometic. Such junk, 80 percent of my rigs problems are with dometic
__________________
12 Blue Elite #6296 38RS3
08 chevy C3500
09 yel spyder toad
Carny Bill is offline   Reply With Quote
Old 03-31-2013, 09:46 AM   #13
rotaxman
Senior Member
 
Join Date: Jul 2005
Location: Liberty Mo (Suburb of Kcmo)
Posts: 559
Agree

Carny,
Couldn't agree more about Dometic if its Dometic its junk.

As always good camping
Joyce and Jerry
__________________
Jerry Sharp
Joyce McAlpin
Two Lives One Dream
2000 F 450 V10
5.38 gears trailer special
Automatic 4R100
20000# Reese Hitch
Trail Air Suspension and Pin Box with Tri Glide
Honda 4500 ex
Hughes Internet
Garmin 2720 talking GPS
Pressure Pro
Junk frame 2009 38TKSB3 #4750
rotaxman is offline   Reply With Quote
Old 03-31-2013, 09:49 AM   #14
rotaxman
Senior Member
 
Join Date: Jul 2005
Location: Liberty Mo (Suburb of Kcmo)
Posts: 559
Rodeworthy

Don,

Haven't heard from you for ever. Hope you and Stella are doing well and that everything is going good.

As always good camping
Jerry and Joyce
__________________

__________________
Jerry Sharp
Joyce McAlpin
Two Lives One Dream
2000 F 450 V10
5.38 gears trailer special
Automatic 4R100
20000# Reese Hitch
Trail Air Suspension and Pin Box with Tri Glide
Honda 4500 ex
Hughes Internet
Garmin 2720 talking GPS
Pressure Pro
Junk frame 2009 38TKSB3 #4750
rotaxman is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3

All times are GMT -5. The time now is 04:44 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
×