You do have enough gen power to do almost everything at the same time--BUT, DRV wires the circuits so they aren't balanced correctly. You should find out what runs on each breaker (circuit)--bet you will find too many items wired to one breaker.
On my '05, I had the same gen--now it is on my '15. On the '05, it ran most things I needed, but just had to be sure that when both ACs were on, that I didn't decide to run the microwave and a blow dryer--I could pull 47 amps without a problem occurring.
How many things do you have on when you are running the gen--anything more than just the 2 ACs?